Reply to comment by ARowzFocuz in EV Charger Installation Recommendations by ARowzFocuz
re: hardwire or plug-in - another factor is, you can swap out a failed charger more easily in the future if it is not hardwired. But, yeah - think about what you want for #2 and #3 before you get quotes, you'll probably want to have the charger picked out before you can spec the installation to be on the safe side. The 240v plug in an outdoor rated box was only like 30 bucks, so pretty low cost compared to the total cost of the install.
ARowzFocuz OP t1_iu5prhk wrote
Great point! I imagine doing plug-in would probably be less expensive, too?
tuctrohs t1_iu74ooj wrote
No, plug in can add $100 to $200. You are on the 2017 code still, so a GFCI breaker probably isn't required, but it would be a good idea, and it is about $100 more than a regular breaker. And a good quality receptacle that is up to the job for EV charging can be $50 to $100. Cheap one fail too often under that continuous operation.