Submitted by Ng3me t3_11cjb6j in philadelphia
eleboil t1_ja5yegd wrote
If that is the Fill, where is the vent? Do you have oil heat? so many questions as an oilman.
signifywinter t1_ja6k81s wrote
There is a small pipe above the fill that was probably where a button whistle was, if it ever existed.
I wouldn’t be surprised if the whole thing is improperly installed. In other words, the button whistle may be the only vent and there may be no associated main vent with weighted cap. Cases like this are very dangerous because the tank can’t vent fast enough while being filled and can lead to tank failure.
Not saying that’s the case here, but the amount of leaking can also be indicative of back pressure from inadequate venting.
cerialthriller t1_ja67eqf wrote
Lol probably over filled cuz there was no whistle
eleboil t1_jaaama7 wrote
This is most likely the case.