picklehaub t1_jcy8vd5 wrote

I’ve sold about a million gallons of #2 this year and haven’t seen any recurring issues.

You said primary was replaced, what I have seen is a bad primary get put in and cause intermittent failures. What did they put in?

6

interweb_gangsta OP t1_jcyctnt wrote

So primary was replaced to fix this issue, but new primary did not make a difference. Analog honeywell was replaced with something else (digital and expensive). Will edit this later with make and model. At work now so can't check.

1

picklehaub t1_jcyfo2b wrote

Did they replace the transformer too?

Most likely you got the resideo 7284 primary or the Beckett genesis. Both are good controls but can be done in by failed transformer.

3