Submitted by G0BLINxKING t3_10lds90 in DIY
G0BLINxKING OP t1_j5wg86i wrote
Reply to comment by ThisIsNotAFarm in Bonding Sub Panel to Main Panel Question by G0BLINxKING
Are you saying that the neutral in this photo (black and yellow) was improperly placed? I am glad I was right in my initial thinking then. I will need to fish a ground from this panel back to the main.
TheSearingninja t1_j5x2zje wrote
No the neutral is fine how it is. You will just need to make sure there is no bonding jumper that goes from the ground bar to the neutral bar in the sub panel. You don’t need to run a ground back to the main ground. What you have to do is to have the subpanel isolated between neutral and ground so that they are not bonded there. You can drive a ground rod near your subpanel and have that as your ground for your subpanel but again making sure your subpanel is not bonded with the neutral bar.
ThisIsNotAFarm t1_j5xv66n wrote
Only because it'd be exempted as an existing installation https://imgur.com/86IshHN.jpg
Viewing a single comment thread. View all comments