I finished building a detached garage on my property that previously had power ran from the main to a sub panel in the shed that has now been demoed and replaced. Do I need to fish a ground from the sub to the main so that the sub panel would be bonded to the main panel ground/neutral bar?
I have the wiring to the outlets and lights complete, but I am needing some help on this panel portion.
The previous set up in the shed was -- power coming in off the main panel (two hots and a neutral), and a bare copper wire from the sub panel into the ground and attached to a grounding rod, no ground back to the main. This is incorrect right? I need the sub grounded/bonded back to the main panel right? I have researched this before and found videos/articles of both ways being done and am still not sure what the correct way to go about this is.
**If I need to clarify anything, please let me know**
Photo taken before demo of shed. (Power was shut off at main before demo)
​
ThisIsNotAFarm t1_j5w7oyo wrote
IIRC neutral/ground MUST NOT be bonded at the subpanel. The subpanel should have two bars, the neutral should be isolated. Ground in the sub should be connected to the main ground, the ground rod should be tied into the sub ground.
But you should definately check with a sparky