Submitted by bwLearnsProgramming t3_zt1p2o in DIY

So my bathroom fan hasn’t been working since we moved into this house about a year ago. Today I decided to try and take a swing at it to no avail. So I am hoping someone here can help me out. The power at the switch reads .3 volt when off and 0 bolts when on. Same reading where the fan plugs in inside the fixture. The fan does not work even when plugged straight into an a known working outlet. The light inside the fixture reads 120 and works fine. Is this a case of replacing the fixture ? Is there more troubleshooting I can do ?

9

Comments

You must log in or register to comment.

Joecool2008 t1_j1b70di wrote

Sounds like the motor has gone bad, at least. Probably needs to be replaced, depending on the age of the house and fixture.

4

Joecool2008 t1_j1b7nmt wrote

I have limited experience, but depending on the fixture there can be (note can be) a smaller fuse inside the motor that could interrupt the flow. Might find a part number and see if there's a manual running around the internet.

2

Big-Spend-2915 t1_j1c6mbx wrote

Your switch should be reading 120, coming in when it is off. If it's not, then you have an issue prior to the switch.
Without seeing how your switch box is set up, it would be hard to tell you where and how to proceed right. It depends on where the power is feeding first.
If you can post some pics, that would help too.

3

SocketWrench t1_j1c8k59 wrote

If it is a bathroom fan with a heater, check to see if there is a breaker for it that may have tripped? These can draw a lot of power and often have a dedicated breaker.

1

muckpucker t1_j1czbaq wrote

You need both a switch and a fan motor.

1

robosmrf t1_j1d0up8 wrote

Need to trace back and find where there is 120v and then troubleshoot from there out.

It could be a switch, the unit itself, or even a bad breaker if the heater is high load and the house is older breakers do go bad.

3

ToolMeister t1_j1dcgz4 wrote

You should have power at the switch at least, no matter whether the device is broken or not.

This leads me to believe the problem is upstream of the switch. If your switch doesn't have a neutral (only hot in, switched hot out) it likely gets power from the fan's electrical box.

Since you said the light fixture still works (combined in the fan?) your problem likely is located behind the fan or wherever it gets its power from.

Could be a loose wire nut, or a shorted/melted connection within the fixture. Take it down and inspect all connections.

Since you said the fan doesn't work even when connected to working power, that means it's definitely gone

3

Alwayssunnyinarizona t1_j1dh1e9 wrote

If it is set on AC, I agree with other posts about something upstream like a tripped breaker. There should be 120V at the switch.

I ask because I often go between testing AC and DC and sometimes forget that I have it set to DC when testing and AC circuit, and vice versa. That low 0.3V is often what reminds me to change it.

2

bwLearnsProgramming OP t1_j1dh1m9 wrote

So behind the switch there is 2 incoming sets of wire, the one that goes to the lights, and the one that goes to the heater and fan. No breakers are flipped at all. Is there a way to follow the wire with no power back to the breaker ? (To check for a bad breaker possibly) or could I cap off the other set and use the wires from the lights to power everything if I replace the unit ?

1

argon561 t1_j1e60a9 wrote

Is the fan maybe humidity controlled? Any small dials / knobs that are visible on it's back? We had such a bathroom fan, and the humidity detector was faulty, but luckily, twisting the "sensitivity dial" to max, just kept the fan on continuously.

Other than that, does it spin if you just push it? As in; is it able to rotate freely?

Might also be nice to know what make and model it is if that's available =)

​

One thing that stood out, was that you measured only .3 volts at the switch? as in 300mV?.. That's absolutely nothing, so either there is no available power there, or something on that line is short-circuited (which would drop the potential to nearly 0 volt) but that would also cause any fuses/circuit breakers to pop.

1