On lighting like that, the ground connection is not really needed, similar to what cbrysncu said
StihlHead460 t1_ixkuvef wrote
This is not necessarily accurate advice
CloneClem t1_ixnrgoy wrote
Not true. If the lamp socket only has a black and white wire and there isn’t a lot of metal like a ceiling fixture, a ground wire serves no purpose
StihlHead460 t1_ixp82pn wrote
Wrong. See NEC 250.4(A)(4) and 110.3(B)
StihlHead460 t1_ixp84s1 wrote
And OP clearly stated that the mfg provided an equipment ground.
CloneClem t1_ixq8c70 wrote
And he also said the existing lights had no ground. They were fine
hahvaggevabba OP t1_ixjm3re wrote
Thank you so much!