Submitted by skinnywolfe t3_ytjee6 in DIY
ttraband t1_iw4k1db wrote
Reply to comment by skinnywolfe in Running wire to power this 20x10 shed for an office. What wire do I need? by skinnywolfe
I’d still add a third circuit (outlet or two) for future expansion, unless the walls are going to be open/a, then it’s easy to add at any time. Often rooms are wired so outlets on parallel walls are one circuit, adjacent walls are differential circuit.
tsaico t1_iw52mjf wrote
Honestly, just do a pull string if you are not doing the 3rd now. Save yourself the cost now, but make it as easy as possible to do it when the time comes. Also, do no smaller than 1" sched 40.
Viewing a single comment thread. View all comments