Reply to comment by dominus_aranearum in Garbage Disposal wired directly into Dishwasher - fixing wiring and adding outlets by TonyFugginMontana
Isn’t an exception to this when the switch box and wiring is accessible? So unless op is moving switch to wall it’s unnecessary?
dominus_aranearum t1_iy9r0gb wrote
I'm wrong. Not a lighting load anyhow.
404.2(C)(7)
who-really-cares t1_iy9r8qw wrote
Just found the code for anyone interested.
404.2(C) Switches Controlling Lighting Loads.
The grounded circuit conductor for the controlled lighting circuit shall be provided at the location where switches control lighting loads that are supplied by a grounded general-purpose branch circuit for other than the following:
(1) Where conductors enter the box enclosing the switch through a raceway, provided that the raceway is large enough for all contained conductors, including a grounded conductor
(2) Where the box enclosing the switch is accessible for the installation of an additional or replacement cable without removing finish materials
(3) Where snap switches with integral enclosures comply with 300.15(E)
(4) Where a switch does not serve a habitable room or bathroom
(5) Where multiple switch locations control the same lighting
load such that the entire floor area of the room or space is visible from the single or combined switch locations
(6) Where lighting in the area is controlled by automatic means
(7) Where a switch controls a receptacle load.