rivalarrival t1_iy9ps8h wrote

Can you cite this? The only reference I've found is to 404.2(C), which clearly specifies that it applies to switches with lighting loads. A garbage disposal is certainly not a "lighting load".

Further, there is specific exception in 404.2(C) for "receptacle" loads, which is what OP is trying to set up.