slashfromgunsnroses t1_it8i1x6 wrote

Not really - if the breaker is dimensioned larger than the outlet material you could overload the outlet material by adding too many appliances. If the breaker is dimensioned as the outlet rating the breaker will trip if theres too much current passing through the outlet.

1

pyrodice t1_it8ia58 wrote

If the breaker is rated the same as the outlet, and the breaker trips, that is good. You don't want to start a fire in the outlet. You always want a circuit breaker to trip before excess heat is concentrated at another connection point.

1

slashfromgunsnroses t1_it8im6z wrote

Exactly.

But the other guys slammed on me for stating this simple fact...

1

pyrodice t1_it8k5o4 wrote

I think you should go back and see what you said and see if you misphrased something, then.

1

slashfromgunsnroses t1_it8t0zo wrote

Im not sure what that would be - help me out. Think I was pretty clear in my first comment

> You need to change your breakers to 10 amps also, otherwise you risk unintentionally overloading the outlets/wires or whatever is the "bottleneck".

1