nocturnal311 t1_ir2nuge wrote
Reply to comment by Loon610 in Wiring EV Charger by Loon610
If it fits under the terminal it should be fine
aimfulwandering t1_ir3gmum wrote
I mean, no not really? The manual indeed does call for 8awg max, and also calls for crimp connectors: https://grizzl-e.com/wp-content/uploads/2022/09/Grizzl-E_Generation2Firmware_Manual_V1.8.pdf
That’s a pretty horrible terminal block design IMO, but it is what is it is.
I’d recommend bringing your 6WG to a disconnect, and then wiring #8 thhn or thwn in the short piece of conduit from the disconnect to the EVSE. Or, alternatively, just install a NEMA 14-50 outlet on the #6 and plug it in.
Check your local code though: a disconnect may be required anyways.
Viewing a single comment thread. View all comments