Viewing a single comment thread. View all comments

Loon610 OP t1_ir1i3vo wrote

Reply to comment by limitless__ in Wiring EV Charger by Loon610

Thanks, for the info. That’s the charger I’m looking at, I noticed the owners manual called for 8 gauge, and my understanding has always been unless it stats otherwise that’s what you have to use. I emailed them asking about the 6 gauge, but haven’t got a response. Did you ask them or just wire it up and figure it out that way?

2

nocturnal311 t1_ir2nuge wrote

If it fits under the terminal it should be fine

1

aimfulwandering t1_ir3gmum wrote

I mean, no not really? The manual indeed does call for 8awg max, and also calls for crimp connectors: https://grizzl-e.com/wp-content/uploads/2022/09/Grizzl-E_Generation2Firmware_Manual_V1.8.pdf

That’s a pretty horrible terminal block design IMO, but it is what is it is.

I’d recommend bringing your 6WG to a disconnect, and then wiring #8 thhn or thwn in the short piece of conduit from the disconnect to the EVSE. Or, alternatively, just install a NEMA 14-50 outlet on the #6 and plug it in.

Check your local code though: a disconnect may be required anyways.

1