Submitted by onemoreburrito t3_11y1bte in DIY
Just built a car port, want to run electric for now to support plug in lights and an out let (standard 15A)
Later in I want to make it easy to add a 240v car charger(48A)
Carport is 75ft from breaker box, 200a service on main box, plenty of knock outs.
I am thinking I can run 8/3 in conduit and wire up 1 pole to the 120v outlet to install now. Leaving the second pole unconnected for now, I would use a 50a dual pole breaker. Does this make sense? Would it work?
Adam2013 t1_jd5vt1r wrote
Nononono
Don't do this. You're thinking in the right direction though.
If the receptacle is only rated for 20 Amp even though the wire is over sized, you breaker for the lowest rated component. In this case, the the receptacle.
Use a 20a breaker.
As far as connecting the receptacle, use a 12 gauge pigtail. It's not rated for 8awg