Teamfreshcanada t1_jd6rq79 wrote
Electrician here. If you are planning to add a 48a EV charger, you need to understand that an EV charger is considered a 'continuous' load. Meaning you need to treat it as being 1.25x the rated load: eg 48 x 1.25 = 60a. This needs #6 wire, not #8.
And for the cost, I would look at running an aluminum acwu armoured cable to the garage for a 100a subpanel. Where I'm at, practically the same cost as running #6 or #8 3 conductor in a conduit. Then, off the sub-panel, you can run lights, outlets, EV, etc. Gives you more flexibility down the line. Just be sure to treat your terminations with anti-oxidant if you go aluminum, and ensure your panel lugs are rated for aluminum conductors (most are).
I'm in Canada, so I'm trying not to go too much into code rules, because they're different up here, but the continuous load stuff is for sure the same. Check with a local licensed electrician for any specific questions you might have.
onemoreburrito OP t1_jd7jwbs wrote
The breaker set up is where I landed after further research. I think I'll just run oversized wires once with the right size breaker to an outlet later. I can expand it to a sub panel to manage distribution to additional circuits at the carport. It's all exposed so no need to tear up walls or anything like that. This should give me good flexibility with one wire run. Thanks for the insights
zuki4life t1_jd7d82z wrote
Definitely for an ev run at least 6