craigcoffman t1_je9kr23 wrote

That 'lazy p.o.s.' was probably the previous homeowner. They probably didn't have the know how or the determination to add a switch & run wire.

2

Madams135 OP t1_je9r0ol wrote

I think you hit the nail on the head. Assuming this wasn't originally a fan, but just another light.

2

PandasWhoLoveToLimbo t1_jeacwc9 wrote

In that case, while you're poking around up there you should also check that the ceiling electrical box that they mounted it on is rated for fan use. It needs to be either drilled into a ceiling stud, or bracketed between two ceiling studs with a metal bar, and if it was originally a light then the builder probably wouldn't have bothered to secure it super well. If its the wrong type of mount then your fan could fall at any time.

1

armorer1984 t1_je9qt4k wrote

I am a non-discriminatory accuser. Doesn't matter who it is. Contractor, homeowner, "a buddy who....", none are immune in my eyes. If you're gonna do something, do it at least 3/4 assed. Not running that second 14/2 is 1/16th assed at best.

0

Ramen576 t1_jeagxth wrote

Sorry to be that guy, but I am sure you mean 14/3. 14/2 is how this guy got stuck asking us for help in the first place. :)

2

armorer1984 t1_jealru7 wrote

Dang fat finger.

1

imnotsoho t1_jedj4wr wrote

Either one 14-3 or 2 14-2s. Both give you enough wires, one is easier and cheaper.

1